Question:easy

Which of the following control mode is also known as RESET control mode?

Show Hint

Industry lingo: If you hear a technician talk about "Reset rate," they are talking about the Integral gain (measured in repeats per minute). If they talk about "Reset time," they are talking about $T_i$ (minutes per repeat).
Updated On: Jul 1, 2026
  • Proportional controller
  • Integral controller
  • Derivative controller
  • Resonant controller
Show Solution

The Correct Option is B

Solution and Explanation

1. The Function of the Integral Term: The integral action calculates the sum of the error over time. As long as the controlled variable is not at the setpoint (error $\neq 0$), the integral term will continue to increase or decrease the controller's output.

2. The "Reset" Terminology: In the early days of industrial control, operators had to manually adjust the bias ($P_0$) of proportional controllers to eliminate the steady-state offset. This was called "manual reset." Because integral action performs this task automatically by shifting (resetting) the proportional band until the error is zero, it became known as the

Automatic Reset or simply the

RESET control mode.

3. Mathematical Representation: $$u(t) = \frac{1}{T_i} \int e(t) \, dt$$ Where $T_i$ is the integral time or "reset time." A smaller $T_i$ results in a faster "reset" of the offset, though it may lead to instability if too aggressive.