Question:medium

Consider a counter-flow heat exchanger with the inlet temperatures of two fluids (1 and 2) being \(T_1 = 300\) K and \(T_2 = 350\) K. The heat capacity rates of the two fluids are \(C_1 = 1000\) W/K and \(C_2 = 400\) W/K, and the effectiveness of the heat exchanger is 0.5. The actual heat transfer rate is (in kW)

Show Hint

Always be careful with units when solving heat capacity problems. Remember: \[ \text{Watts (W)} \rightarrow \text{kiloWatts (kW)} \text{ divide by } 1000. \] Crucially, always evaluate \(C_{\text{min}}\) to calculate maximum possible heat transfer, because the fluid with the smaller heat capacity rate will limit the overall heat exchange process by reaching its thermodynamic temperature limit first.
Updated On: Jun 25, 2026
  • 12
  • 15
  • 18
  • 10
Show Solution

The Correct Option is D

Solution and Explanation