Step 1: List the reservoir temperatures in Kelvin.
Cold side: $T_C = -30 + 273 = 243\ K$. Hot side: $T_H = 20 + 273 = 293\ K$.
Step 2: Use the heat pump COP instead of the refrigeration COP.
For a reversed Carnot engine, the heating COP is $COP_H = \dfrac{T_H}{T_H - T_C} = \dfrac{293}{50} = 5.86$.
This directly gives the fraction of rejected heat to work input, since $COP_H = Q_H/W$.
Step 3: Relate work to the known cooling load.
The two COPs are linked by $COP_H = COP_C + 1$, where $COP_C = T_C/(T_H-T_C) = 4.86$.
So $COP_H = 4.86 + 1 = 5.86$, confirming the value above. Work input: $W = Q_C / COP_C = 70/4.86 = 14.4\ kW$.
Step 4: Get the rejected heat directly.
$Q_H = COP_H \times W = 5.86 \times 14.4 = 84.4\ kW$, the same figure found from the energy balance.
Final Answer:
Using the heating COP cross checks the earlier balance and lands on option (A) again.
\[ \boxed{84.40\ kW} \]